Power Specifications
Power Supply Specifications
65 W AC Power Supply
The 65 W AC power supply is a fixed internal unit for the 5320-24T-4X-XT switch.
Voltage input range
90-132/198-264 47 to 63Hz~
Nominal input ratings
1.5A max at 100VAC and 1.0A max at 240VAC at Full 65 W load
Maximum inrush current
60A at Max 230VAC / 50Hz at 25C
Output
12V @65W
Power supply input socket and cord
IEC/EN 60320-1/C14 AC input receptacles
Power cord wall plug
Refer to Power Cord Requirements for AC-Powered Switches and AC Power Supplies
Efficiency
Minimum 88% at maximum power output
90 W AC Power Supply
The 90 W AC power supply is a fixed internal unit for the 5320-24T-8XE and 5320-48T-8XE switches.
Voltage input range
90-132/198-264 ~ 47 to 63Hz ~
1.2A max at 115VAC and 0.6A max at 230VAC at Full 90W load
130A at Max 230VAC / 50Hz at 25C
Output
12V, 7.5A max, 90W
Efficiency
Minimum efficiency: 85% at maximum power output 115VAC
150 W AC Power Supply
The 150 W AC power supply is a fixed internal unit for the 5320-24T-24S-4XE-XT switch.
Voltage input range
1.8A max at 115Vrms
120A at Max 230VAC / 50Hz at 25C
Output
12V, 12.5A @150W
Efficiency
Minimum 87% at maximum power output
250 W AC Power Supply
The 250 W AC power supply is a fixed internal unit for the 5320-16P-4XE switch.
Voltage input range
3.8A max at 90VAC at Full 250W load
Output
12V, 4.58A max, 54V, 3.61A max, 250W
Efficiency
Minimum efficiency: 90% at maximum power output 115VAC
305 W AC Power Supply
The 305 W AC power supply is a fixed internal unit for the 5320-16P-2MXT-2X switch.
Voltage input range
90-132/198-264 ~ 47 to 63Hzto
Nominal input ratings100-240 V, 50/60Hz, 4A max
Maximum inrush current30A at Max 115V, 60A at 230V
Output12V, 5A max, 54V, 4.5A max 305 W
Power supply input socket and cordIEC/EN 60320-1/C16 AC input receptacles for use with a IEC/EN 60320-1/C15 cord
Power cord wall plugPower Cord Requirements for AC-Powered Switches and AC Power Supplies
EfficiencyMinimum efficiency: 85% at maximum power output 115VAC
550 W AC Power Supply
The 550 W AC power supply is a fixed internal unit for the 5320-24P-8XE switch.
Voltage input range
90-132/180-264 ~ 47 to 63Hz
8.5A max at 90VAC at Full 550 W load
30A at Max 115VAC / 60Hz at 40C
Output
12V, 12.5A max, 54V, 7.4A max 550 W
Efficiency
Minimum efficiency: 87% at maximum power output 115VAC
950 W AC Power Supply
The 950 W AC power supply is a fixed internal unit for the 5320-48P-8XE switch.
Voltage input range
15A max at 90VAC and 7.5A max at 180VAC at Full 950 W load
Output
12V, 14.1A max, 55V, 14.2A max, 950 W
Efficiency
DC Power Supply
The DC power supply is a fixed internal unit for the 5320-16P-4XE-DC switch.
Table 1. Power Specifications
Voltage input range
36 - 72V, 9.8 A max
Nominal input
48Vdc
DC output
12V/120W, 54V/200W
150 W Redundant Power Supply
The 150 W redundant power supply can be used with the 5320-24T-4X-XT and 5320-24T-24S-4XE-XT dwitches.
Table 2. Power Specifications
AC Input
100 - 240Vac, 50-60 Hz, 1.8A max. per PSU
DC Output
12Vdc, 12.5A max. total 150 W max.
Minimum/Maximum Power Consumption and Heat Dissipation
Switch ModelMinimum Power Consumption (W)Minimum Heat Dissipation (BTU/hr)Maximum Power Consumption (W)*Maximum Heat Dissipation (BTU/hr)**
5320-16P-4XE1757246208
5320-16P-4XE-DC2067260256
5320-16P-2MXT-2X12.5 4321875
5320-24T-8XE186050171
5320-24P-8XE2170480375
5320-48T-8XE258564217
5320-48P-8XE30104924629
5320-24T-4X-XT143549119
5320-24T-24S-4XE-XT 259687328
Max PoE Power Budget
Switch ModelPoE Budget
5320-16P-4XE185W
5320-16P-4XE-DC185W
5320-16P-2MXT-2X180W
5320-24P-8XE370W
5320-48P-8XE740W