5520 Series switches support the following power supplies:
The 350 W AC power supplies (part numbers XN-ACPWR-350W-FB and 10953) provide front-to-back airflow and are compatible with 5520-24T, 5520-24T-BASE, 5520-24X, 5520-24X-BASE, 5520-48T, 5520-48T-BASE, 5520-48SE, and 5520-48SE-BASE switches.
The 350 W AC power supplies (part numbers XN-ACPWR-350W-BF and DPS350AB-42 A) provide back-to-front airflow and are compatible with 5520-24T-BASE, 5520-24X-BASE, 5520-48T-BASE, and 5520-48SE-BASE switches.
The 550 W AC power supplies (part numbers XN-ACPWR-550W-FB which provide front-to-back airflow, and XN-ACPWR-550W-BF which provide back-to-front airflow) and the 550 W DC power supplies (part numbers XN-DCPWR-550W-FB which provide front-to-back airflow, and XN-DCPWR-550W-BF which provide back-to-front airflow) are compatible with the 5520-24T-ACDC, 5520-24X-ACDC, 5520-48T-ACDC, and 5520-48SE-ACDC switches .
The 715 W AC PSU-FB (part numbers XN-ACPWR-715W-FB and 10951) provide front-to-back airflow and are compatible with 5520-24W, 5520-12MW-36W, and 5520-48W switches.
The 1100 W AC PSU-FB (part numbers XN-ACPWR-1100W-FB and 10941) provide front-to-back airflow and are compatible with 5520-24W, 5520-12MW-36W, and 5520-48W switches.
The 2000 W AC PSU-FB (part numbers XN-ACPWR-2000W-FB and XN-ACPWR-2000W-F) provide front-to-back airflow and are compatible with 5520-24W, 5520-12MW-36W, and 5520-48W switches.
Pre-Installation Requirements
You need the following tools and materials to replace a power supply:
Thermal protective gloves
AC power cord, if you are not re-using the cord from the removed power supply
Remove a Power Supply
Caution
Disconnect the AC power cord from the wall outlet and from the power supply before removing an AC power supply. Ensure that the DC circuit is de-energized before removing a DC power supply.
Use the following instructions to remove a power supply.
Attach an ESD-preventive wrist strap to your bare wrist and connect the metal end to an appropriate ground point on the rack.
Caution
Power supplies can become very hot during operation. Wear thermal protective gloves when you remove a power supply from an operating switch.
Note the orientation and the airflow direction of the installed power supply, and the location of the latching tab on the power supply.
Push the latching tab toward the power supply handle and pull outward on the handle to disengage the power supply internal connectors.
Remove a Power Supply
Note
If you are not installing a replacement power supply, install a cover over the unoccupied power supply bay. Unoccupied bays must always be covered to maintain proper system ventilation and EMI levels.
Replace or Install a Power Supply
Use the following instructions to replace or install a power supply.
Attach an ESD-preventive wrist strap to your bare wrist and connect the metal end to an appropriate ground point on the rack.
If necessary, remove a blank panel from the back of the switch.
Ensure that the orientation of the power supply is correct, and that the new power supply's airflow direction (front-to-back or back-to-front) is compatible with the installed fan modules and any other installed power supplies.
Carefully slide the power supply all the way into the power supply slot.
Install a Power Supply
Push the power supply in until the latch snaps into place.
Do not slam the power supply into the switch.
Note
Be sure to install a cover over any unoccupied power supply slots. Unoccupied power supply slots must always be covered to maintain proper system ventilation and EMI levels.
To install or replace a second power supply repeat this procedure.
After installing a power supply, connect the power cord to the power supply.
If the power supply was an AC power supply, connect it to a grounded AC power outlet.
Warning
Always make sure that the source outlet is properly grounded before plugging the AC power cord into the AC power supply.
If the power supply was a DC power supply, use the provided 2 meter DC power input cable for the DC power supply to ground the power supply and connect the power supply to the power source.
Warning
Connect the chassis ground wire before you connect any power cables.
Connect a DC Power Supply to the Source Voltage
The DC power connection at your facility must be made by a qualified electrician, following these instructions.
Warning
Always make sure that the DC circuit is de-energized before connecting or disconnecting the DC power cables on the DC power supply
Caution
Provide proper connection and strain relief on the DC power cables in accordance with all local and national electrical codes.
Verify that the DC circuit is de-energized.
Attach an ESD-preventive wrist strap to your bare wrist and connect the metal end to an appropriate ground point on the rack.
Tighten the two thumb screws to secure the DC power connector in place.
The installation electrician connects the other end of the power cord to the building power system.
Warning
Before installing, be sure to connect the chassis ground wire before you connect any power cables.
Warning
Before removing, be sure to disconnect the ground wire after you disconnect all power cables
Connect the ring terminal of the yellow and green ground wire to a known reliable earth ground point at your site.
DC Power Cable
Use the following for building the wire harness:
Cable Connector
Wire Color
Pin 1
Yellow/Green
GRD
Pin 2
Black
-48V
Pin 3
Red
RTN
Connect the ring terminal of the red RTN power cable to the positive terminal of the DC power source, and connect the ring terminal of the black -48V power cable to the negative terminal of the DC power source.
Repeat these steps for each power supply.
Leave the ESD strap permanently connected to the rack, so that the strap is always available when you need to handle ESD-sensitive components.